3.6.1 Redistributor power management

At reset, the Redistributors are considered to be powered down. To power up the Redistributors, software must use the GICR_PWRR register.

Note:

This requirement is true for all GIC-600 configurations.

The GICR_PWRR register can control Redistributor power management either by operating through the core, or through the Redistributor.

If operating through the core, each core must program its GICR_PWRR.RDPD = 0 and GICR_PWRR.RDAG = 0 to ensure that the Redistributor powers up. Alternatively, a single core can power up the Redistributor for all cores that connect to the same Redistributor by writing GICR_PWRR.RDPD = 0 and GICR_PWRR.RDAG = 1.

You can use GICR_PWRR.RDG to identify which core shares a Redistributor.

The powerup and powerdown sequences are shown in the following pseudocode:

Power off (setting RDPD to 1):

// Check group not transitioning.
repeat
until (GICR_PWRR.RDGPD == GICR_PWRR.RDGPO)

// Write to power the CPU off.
GICR_PWRR.RDPD = 1;


Power on (setting RDPD to 0):

repeat
  // Check group not transitioning.
  repeat
  until (GICR_PWRR.RDGPD == GICR_PWRR.RDGPO)

  // Write to power the CPU on.
  GICR_PWRR.RDPD = 0;

  // Check access, if RDPD == 0 then powered on.
until (GICR_PWRR.RDPD == 0)

Note:

GICR_PWRR must be accessed using the GICR address space that relates to the core being powered on or off.